SolarEdge PV Label

Status
Not open for further replies.

Zyb

Member
Location
Maine
Occupation
Design Engineer
Commercial Project
Module: (237) Silfab 490 HN (490W)
Optimizer: SE P1101
Inverter: (2) SE50KUS


Can anyone verify my label values. Thank you

DC
Operating Current: 314A = (237 x 490) / 370 = (no. of mod x mod power) / min. operating voltage range ??
Operating Voltage: 208V
Maximum System Voltage: 600V
Short Circuit Current: ??

AC
Rated AC Current: 279A = 2 x 139.5
Nom. AC Voltage: 208V





1667833466739.png

1667833864942.png
1667834496927.png

1667833671597.png
 

Attachments

  • 1667833535054.png
    1667833535054.png
    28 KB · Views: 1

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Your DC numbers are all wrong because of the P1101 DC to DC converters. Your DC short circuit current is 18A and the maximum output voltage is 80V times the number of P1101s you have in your longest string unless it is more than the maximum DC voltage that the inverter can take, which in the case of the SE50KUS is 600V.
 

Zyb

Member
Location
Maine
Occupation
Design Engineer
Your DC numbers are all wrong because of the P1101 DC to DC converters. Your DC short circuit current is 18A and the maximum output voltage is 80V times the number of P1101s you have in your longest string unless it is more than the maximum DC voltage that the inverter can take, which in the case of the SE50KUS is 600V.
Thank you
 

Carultch

Senior Member
Location
Massachusetts
SolarEdge has a whitepaper on labeling your SolarEdge system, that describes the equivalents of labeling a standard PV system adapt to their equipment.
 