Parking lot lighting is circuited 480 volt single phase. 2 hots each lamp AB BC CA. Nine circuits are used, grouped in three circuits to each run. Is the protecting breakers single phase breakers or 3 three phase breaker?
Why do they need to be on 3 pole breakers? I know several companies that make 2 pole breakers for 480 volts.bdarnell said:These circuits need to be on 3 pole breakers.
240.20(B)(3) 3-Phase and 2-Phase Systems For line-to-line loads in 4-wire, 3-phase systems or 5-wire, 2-phase systems having a grounded neutral and no conductor operating at a voltage greater than permitted in 210.6, individual single-pole circuit breakers with identified handle ties shall be permitted as the protection for each ungrounded conductor.
james wuebker said:Why do they need to be on 3 pole breakers? I know several companies that make 2 pole breakers for 480 volts.bdarnell said:These circuits need to be on 3 pole breakers.
Larry, I believe it's 480 single phase that requires 2 hots and a grounding wire. He really didn't tell us how he was controlling these lights also.LarryFine said:james wuebker said:Why do they need to be on 3 pole breakers? I know several companies that make 2 pole breakers for 480 volts.bdarnell said:These circuits need to be on 3 pole breakers.
Because, unless I misunderstand the OP, each circuit is a 3-wire, with loads connected phase-to-phase, one on A-B, one on B-C, and one on C-A.
Pierre C Belarge said:It seems to me the are 3 groups of 3, 2-pole circuits for the lights. In that case, a 2-pole breaker could be installed.
james wuebker said:Why do they need to be on 3 pole breakers? I know several companies that make 2 pole breakers for 480 volts.bdarnell said:These circuits need to be on 3 pole breakers.
Jim
Definitely need a 3-pole breaker, since you have line-to-line loads.uplanddreams said:Thank you for your comments thus far. The 3 phase wire will be run from the breaker to a 3 pole contactor controlled by an EMS then to the parking lot poles. The phase conductors are tapped at each pole for the two phases needed. There is fuse protection for each phase conductor which runs up the pole to the lights.
Not if the supply system is grounded. See 240.20(B)(3).Definitely need a 3-pole breaker, since you have line-to-line loads.
I stand partially corrected: handle ties are permitted in both (B)(2) and (B)(3). The point is that simultaneous manual disconnecting is necessary, even if simultaneous automatic disconnecting is not.don_resqcapt19 said:Larry,
Not if the supply system is grounded. See 240.20(B)(3).Definitely need a 3-pole breaker, since you have line-to-line loads.
dON
In most cases they will not trip the other pole(s).modern handle-tied breakers will, in fact, simultaneously trip from a single-phase over-current.