separation

Status
Not open for further replies.
I am aware of the 2" minimum separation between power and communication wiring. Have following question. After conduit was installed (3/4" rigid), specification changed. I now need to feed several
devices requiring 120vac (maximum 2-3 amps total) as well as supply two cat5 cables. Will I need to have an additional conduit run (its a 2-3 day process) or can I run both in same conduit. I understand there is an NEC exception for UF cable (though I'm not sure electrician could pull it through conduit). Do I have any other options?
Thanks, Bob
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The references may change a bit depending on which Code cycle is in place. but you can look at 800.133 (a)(2) in the '11 and see the exceptions.
 