So the other day I was thinking about a portable system I was working on. It has 480 volt 3-phase coming in that is transformed down to 208-120 for the actual equipment. If this was an SDS, some kind of grounding electrode connection would be required. This is moderately inconvenient for a portable system.
So it occurred to me that if I were to connect the neutral of the secondary side of the transformer to the neutral of the 480 coming in, it would no longer be a separately derived system and thus would not require a grounding electrode.
This seems almost too simple of a solution to me so I'm wondering if I have missed something here.
Being as the neutrals will be connected together eventually via the EGC, I don't see a downside electrically or safety wise, and I'm not convinced that having an extra grounding electrode serves any real purpose.
I haven't had time to look real close at the requirements for such things so maybe I am missing something obvious.