Riser Cable or Plenum cable in an interstitial space

jakeparsons03

Member
Location
USA
Occupation
Engineer
We have electricians who want to run control wire from a device back to the control panel by taking conduit up to an interstitial space then free-air running it back above a control panel and dropping it in conduit to the panel. The interstitial space is technically not a plenum as while it has Make Up Air units, they are piped to the outside and to the occupied space. There are exhaust fans on this level though. Do I need plenum cable or would riser cable work here.

I get the feeling that this is a gray area and it would depend on how your inspector is feeling that day.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
If the space is used to convey air, whether heating/cooling or ventilation, it is considered an air handling or plenum space. Any cable run in that space must be plenum rated.

-Hal
 