- Location
- Windsor, CO NEC: 2017
- Occupation
- Service Manager
1.) NEC Section/Paragraph: 110.3(B)
2.) Proposal Recommends: [revised text]
3.) Proposal: (B) Installation and Use. When listed or labeled equipment is installed, it shall be installed and used in accordance with any instructions included in the listing or labeling.
4.) Substantiation: As this section is currently written, it seems to require that listed or labeled equipment is required to be used. This would add clarity that unlisted equipment can be used, if it is approved by the Authority Having Jurisdiction.
2.) Proposal Recommends: [revised text]
3.) Proposal: (B) Installation and Use. When listed or labeled equipment is installed, it shall be installed and used in accordance with any instructions included in the listing or labeling.
4.) Substantiation: As this section is currently written, it seems to require that listed or labeled equipment is required to be used. This would add clarity that unlisted equipment can be used, if it is approved by the Authority Having Jurisdiction.