im helping a buddy whos building a duplex. Im doing a service calculation, to confirm both sides can be run off of 1 200 amp service.Both combined are 1100 sq ft, 2 4Kw water heaters, 2 10Kw heater, no laundry facilities to be installed. (1) lighting load = 3300 (2) small appliance circuits = 6000 (3) demand on above =(ist 3000 at 100% = 3000)+ (3001- 120000 at 35%= 2205)= 5205 (4) larger of a/c or heat 10kwX2 =20Kw. (5) clothes dryer at 5Kw. this is where my question lies, on part 2 above you can omit the laundry circuit if not installed, however i see no such exception to dryer circuit .(6) 2 ranges at demand factor of 11Kw.(7) total =44205 w/o dryer, =184 amps or 54205 = 226 w dryer. we want to save money and not go up to the next size service but we don't want ot burn up the 200 amp panel. this calculation doesnot include the refrigerators or vent hood or vent in the bathrooms. should these be included in the calculation or not.
thanks for any help will Dalrymple