redundant ground in patient care areas

Status
Not open for further replies.

na112233

Member
I believe the insulated redundant ground to receps in patient care areas need to be bonded to box. Anyone agree or disagree? These are not isolated ground receps.
 

ryan_618

Senior Member
Re: redundant ground in patient care areas

Yes, they must be bonded to the box, per 250.148. Without bonding them to the box you lose the entire concept of decreased impedence in the fault clearing path.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: redundant ground in patient care areas

This would also apply to EGC's installed in metallic raceways not in patient care areas.
 