1. This sounds a little personal.

2. Did you offer any input to your team member?

3. What does Engineering have to say about the installation. Does it meet site specs?

4. There some support issues with the LFMC.

5.The starter below the installation looks like it was previously installed.

Pjholguin :cool:


bypynyte.jpg
saseqybe.jpg



I'd like to get other opinions on this installation a co-worker recently did. Personally feel it?s weak using unistrut and should have been welded using angle steel and channel.
Sent from my HTC6435LVW using Tapatalk[/QUOTE]
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
It appears to be a temporary installation, and more than adequate for that purpose. Does not look like a good permanent install but probably no code issues.

I do not see any obvious code violations other than maybe not supporting the flex adequately.

Unless there is a job spec prohibiting strut in favor of welded steel for temp installations, I see no issue here.

My biggest objection would be to mounting the electrical equipment on the railing. Most job specs prohibit that IME. The railing looks about as bad as the electrical installation.
 