Is a peice of PVC that measures 22 inches long used to protect wires considered a raceway or a protection device and where do I find this explained in the code book, due to the fact of derating the wires.
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: raceway

This may help...
310.15(B)(2)(a)More Than Three Current-Carrying Conductors in a Raceway or Cable. Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(2)(a).
 