Question

Status
Not open for further replies.

sly73.sp

Member
Location
US
We have a metters sub panel and we build a house and we have 550ft from the metter panel do we have to pull ground from the Metter panel?

Sent from my SM-G928T using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
That's the Code the OP states is current in his jurisdiction. Your 1st clue !
 

kwired

Electron manager
Location
NE Nebraska
Is just a moderate sized house if there is a 550 foot run in/on it:cool:

Possibly has a meter and a 550 foot run to the house?

If so then the need for an EGC depends if the meter has a service disconnecting means associated with it. Just a meter with no disconnect/overcurrent protection - the load side conductors are still considered service conductors. Throw a (per defined) service disconnecting means in at the meter location, and the load side conductors are feeders and will require an equipment grounding conuctor.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
That's the Code the OP states is current in his jurisdiction. Your 1st clue !
Well, he says he is in Anaheim too and we (California) are still on the 2011 code, at least for now and MAYBE 2014 this month (it typically lags by 3 years). So either he doesn't know what "code cycle" means, or he is not really an electrician. But we are definitely not 2015.
 