Gentlemen, I cant seem to confirm 100% that this installation would fly.
I am wanting to parallel a 800 amp CT service.
Typically I would terminate in a 800 amp outdoor panelboard with a 6 breaker capacity. I would then take 2 or 3 breakers and feed multiple "tenant" panels. The 6 space panelboard would not have a main breaker.
What I am trying to do is parallel through the CT cabinet but terminate each set of conductors at a 400 amp enclosed breaker and each enclosed breaker feed a seperate panelboard in the tenant space.
I have read and re-read 230 but where I guess I am getting tripped up is the gray area of the disconnects being in a "group"
Can anyone offer some insight on this?