i have a 100 amp service 120/240 with a #6 GEC gowing to a ground rod at what points on the service can i connect the other end of the GEC TO THE SERVICE.
 

russ

Senior Member
Location
Burbank IL
Re: question from student

250.36(F) At any point from the grounded side of grounding connection at the service equipment or the system disconnecting means.

250.53(D)(2) If it's a supplemental electrode, it can be bonded to the grounding electrode conductor, the grounded service conductor, the non flexible grounded service raceway or any grounded service enclosure.

[ March 03, 2004, 03:13 AM: Message edited by: russ ]
 

russ

Senior Member
Location
Burbank IL
Re: question from student

Strike the 250.36(F) reference.

250.24(B)is where you will find it.