Does a generator terminal require 90c rating?

A test I recently took implied that a lug terminal on a portable generator should be AL9CU rather than plan AL/CU. This is for a non-emergency site generator not connected (usually) to a building. I get into this stuff for events held away from power supplies. I've been poking around trying to find something that says anything about it one way or another.

Any references?
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
I was asking if the terminals need to be 90C.

No, you would be hard pressed to find a 90 degree lug in most any piece of equipment.
And every other connection would have to be good for 90 degrees also.
 