Article 680-22 of the NEC states " It shall not be the intent of this section to require that the number 8 solid copper bonding conductor be extended or attached to any remote panel board, service equipment or grounding electrode, but only that it shall be employed to eliminated voltage gradients in the pool area".
I was under the impression that the bond wire should start at the panel board and end near the filter? Is this not true? If so, I assume that the bonding wire just has to encircle the pool area and connect to metal ladder pockets, diving board jigs and the frame work of the pool then end at the pump.
[ April 24, 2003, 07:19 AM: Message edited by: fmignella ]
I was under the impression that the bond wire should start at the panel board and end near the filter? Is this not true? If so, I assume that the bonding wire just has to encircle the pool area and connect to metal ladder pockets, diving board jigs and the frame work of the pool then end at the pump.