Plenum approved lighting fixtures

Status
Not open for further replies.

papanick

New member
Are there any code requirements for the labeling and/or testing of lighting fixtures when they installed in a return air plenum HVAC system. This is not a question for any fire rated assemblies appliations.
 

ryan_618

Senior Member
Re: Plenum approved lighting fixtures

They must have a flame spread index of not more than 25 and a smoke developed index of not more than 50.

This shouldn't be a problem if they are made of steel. :)
 

esox39

Member
Location
Chicago, IL
Re: Plenum approved lighting fixtures

300.22(b)......enclosed gasket-type luminaires (fixtue) shall be permitted. These fixtures are commonly call "plenum rated".
 