What is the best way to bond parking lot lighting poles.I am installing 32 new concrete base 20 foot steel poles.I use to bond one leg of anchor bolt to one of the one inch hold down bolts and pigtail from their.Any suggestions?
Thanks, work is in southern California Los Angeles area.
 
Re: Parking Lot Lights

No I am not using to ground my lights.I am using the grounding electrode from my service to ground lights and pole.
The old concrete poles usually have a #8 solid bonded to footing re bar and then to steel structure of pole.
 

luke warmwater

Senior Member
Re: Parking Lot Lights

Originally posted by harborrick:
I am using the grounding electrode from my service to ground lights and pole.

OK.
(generalized):The GEC is required with the circut conductors.

The old concrete poles usually have a #8 solid bonded to footing re bar and then to steel structure of pole.

This is not an NEC requirement. If you want to use it, connect it to the GEC.
 

hurk27

Senior Member
Re: Parking Lot Lights

That's ok Luke I'm starting one of those week's already too. Cold and rainy YUK! and the brain is all froze up LOL :roll: :confused:
rolley.gif
 