Can anyone give a code reference about panels connected to an emergency system must be fully rated? We recently submitted some switch gear submittals that were returned noted. The comment stated "NEC requires panels connected to an emergency system to be fully rated". I am not trying to argue this, however, we have done many of this exact buildings and have never had this comment before. I have looked but cannot seem to find the code they are referencing.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Series rated systems are not selectively coordinated and cannot be made so. 700.32 requires selective coordination. Note that is a 2023 section number and I believe it was in a different section in older codes.
 

PbMXer_218

Member
Location
Largo, Florida
Occupation
Licensed Electrician EC
Series rated systems are not selectively coordinated and cannot be made so. 700.32 requires selective coordination. Note that is a 2023 section number and I believe it was in a different section in older codes.
It is 700.32 in the 2020. Thank you for the help! Greatly appreciated!
 