I have a 200a service in a home that I need to connect/backfeed 2 - 50a PV breakers to. I can either increase the service or re-configure the existing service. Any thoughts
If you downsize the main breaker it must be less than 140A.I have a 200a service in a home that I need to connect/backfeed 2 - 50a PV breakers to. I can either increase the service or re-configure the existing service. Any thoughts
1) Upgrade the service (if the customer is willing to pay)
Not that it is likely to happen in other jurisdictions, but Los Angeles DWP is particularly anal about this point: They will not allow the panel rating (regardless of the actual main breaker installed) to be higher than the nominal service size. This causes all kinds of grief for solar installers there.You don't need to upgrade the service, you need to upgrade the busbar rating of the main panelboard.
Granted, it is major surgery to do that still. But at least you wouldn't need to get the utility involved to change any equipment upstream this device. Provided that you can fit a 200A breaker in a 400A panelboard.
You don't need to upgrade the service, you need to upgrade the busbar rating of the main panelboard.
Granted, it is major surgery to do that still. But at least you wouldn't need to get the utility involved to change any equipment upstream this device. Provided that you can fit a 200A breaker in a 400A panelboard.
Seems like it would cause grief for others too. Around here a 200A feed through panel can be bought for about $75 less than a 150A.Not that it is likely to happen in other jurisdictions, but Los Angeles DWP is particularly anal about this point: They will not allow the panel rating (regardless of the actual main breaker installed) to be higher than the nominal service size. This causes all kinds of grief for solar installers there.
What if the 200a MB panel is converted to a sub-panel with a 200a main disconnect. Does the 120% rule still apply to the sub-panel - it no longer has a main breaker to include in the calculation
Also, does the 120% rule apply to the service, the main breaker, or the bussbar rating the solar breakers are connected to ?
And, in the case of a subpanel, the feeder conductors to that sub. (At least according to some AHJs.)The busbar.
Not that it is likely to happen in other jurisdictions, but Los Angeles DWP is particularly anal about this point: They will not allow the panel rating (regardless of the actual main breaker installed) to be higher than the nominal service size. This causes all kinds of grief for solar installers there.
What if the 200a MB panel is converted to a sub-panel with a 200a main disconnect.
What if the 200a MB panel is converted to a sub-panel with a 200a main disconnect. Does the 120% rule still apply to the sub-panel - it no longer has a main breaker to include in the calculation
If the sub is MLO then you use the size of the feeder breaker in the main.
It is only in a supply side connection that you do not have a supply breaker to count.
Correct. Combiner-only panels are a special case.It depends on the AHJ. I have designed load side connected systems that used AC combiners sized only to accommodate the inverter breakers which passed muster with the AHJ.
And, in the case of a subpanel, the feeder conductors to that sub. (At least according to some AHJs.)