Is it a requirement that motors have overloads? I understand why motors have overloads. The branch OCPD is only providing short circuit protection, and without it there is absolutely no overload protection. I have a 1/2HP single phase motor that does not have an internal overload, and the question has been asked "I know I need one, but it is an absolute requirement that I have an overload."

I've explained the "why's" to them, but is there an NEC or NFPA79 code that absolutely requires it?
 

fifty60

Senior Member
Location
USA
I seem to remember reading that a single thermal magnetic circuit breaker could be used in place of the short circuit OCPD and separate overload....
 

fifty60

Senior Member
Location
USA
I've read through section III of article 430 (NEC 2011) and do not see the exception that allows you to use a single thermal-magnetic breaker or dual element fuse as short circuit AND overload protection....does this exception exist anywhere inside the code?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I've read through section III of article 430 (NEC 2011) and do not see the exception that allows you to use a single thermal-magnetic breaker or dual element fuse as short circuit AND overload protection....does this exception exist anywhere inside the code?

Section III of Art 430 permits a "Separate Overload Device." This can be fuses or a circuit breaker. But keep in mind that there is no "next size up" rule for overload devices.
 

fifty60

Senior Member
Location
USA
So a dual element fuse or a thermal magnetic breaker would qualify, even though it would be serving the dual purpose of short circuit protection and overload protection?
 

fifty60

Senior Member
Location
USA
430.32(1) says "Motors with a marked temperature rise 40 C or less 125%". I would get this information from the insulation rating right? In this case it is Class F insulation. The temperature rise for this motor, with a 1.25 service factor, is much more than 40 C right? It would be closer to 115 C? Or would that not be the information that is being asked for in NEC 430.32(1)?

Also, I cannot tell if the "Motors marked with service factor 1.15 or greater" and "Motors with a marked temperature rise 40 C or less" are anded together, or if they are or'd. Since I know the service factor is 1.25, can I then ignore the temperature rise requirement for this particular clause?

I actually found the temperature rise in the data sheet. It is 67 C at rated load and 80 C at service factor load....this is above the 40 C, does that mean I have to size at 115% or can I size at 125% based on the "service factor greater than 1.15"...
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The answer, IMO, is not a simple one. Details matter.
Possibilities: Is it Automatically started ? If so, 430.32(B)
For non-automatic start, see 430.32(D)
Is it on a General-Purpose branch circuit ? If so 430.42(A)
(which also directs you to G P circuit cord & plug connected 430.42C)
 

fifty60

Senior Member
Location
USA
It is an automatic start motor. It will be an air circulator motor inside of a refrigeration/oven chamber. Refrigeration equipment itself is not a general purpose equipement. Would the motor inside be considered a general purpose branch circuit inside a specific purpose application? I believe regardless, I am directed back to 430.32 (1). Service factor 1.25, temperature rise is above 40...is 125% rounded down permissible?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
The answer, IMO, is not a simple one. Details matter.
Possibilities: Is it Automatically started ? If so, 430.32(B)
For non-automatic start, see 430.32(D)
Is it on a General-Purpose branch circuit ? If so 430.42(A)
(which also directs you to G P circuit cord & plug connected 430.42C)

I agree. Especially when you are considering anything less than 1 HP. Above 1 HP things are a little more straight forward.
 

fifty60

Senior Member
Location
USA
I have it mostly figured out except for the fact that it is a 1.25 service factor motor, which allows 125% rounded down, but its temperature rise is above 40 C, so I would have to go to 1.15%. Is this "and" or "or"? Does the service factor of 1.25 alone allow 125% rounded down, or does the temp rise being above 40 C mandate then that I would have to use 115% rounded down?
 

rlundsrud

Senior Member
Location
chicago, il, USA
I know that they exist, but single phase motors that don't contain internal thermal protection are quite rare. Have you verified that this motor doesn't have this?

Bob
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I have it mostly figured out except for the fact that it is a 1.25 service factor motor, which allows 125% rounded down, but its temperature rise is above 40 C, so I would have to go to 1.15%. Is this "and" or "or"? Does the service factor of 1.25 alone allow 125% rounded down, or does the temp rise being above 40 C mandate then that I would have to use 115% rounded down?

I see it as an "or".
 