For a GEC, you must bond entries and exits. However, I think many misinterpret the requirement to think that means all raceway entries and exits. It is [in fact] conductive envelopment entries and exits. You only have to bond directly where the GEC transitions from conductive envelopment to non-conductive envelopment or completely exposed.
Let's say we have a combined EGC/GEC of PV system connected in MDP. Being the enclosure is metallic, the GES GEC(s) are bonded to the enclosure. The metallic raceway must be bonded... but it can be bonded to the enclosure using a bonding locknut. On the other end, the inverter enclosure is metallic, so the EGC/GEC is bonded to the enclosure. The raceway is bonded to the enclosure with a bonding locknut. No bonding bushings. No bonding jumpers.
Thanks for the clarification. I'd like to put it in my own words to make sure I'm understanding this.
When you have a GEC routed through a continuous system of metal raceways and metal enclosures, you only need to connect the GEC via a bonding bushing to the raceways at the origin and destination of the GEC. All intermediate connections can have electrical continuity established by ordinary grounding practices (Myers hubs, standard locknuts, sealing locknuts, etc).
It is only when the raceway/enclosure system breaks electrical continuity (by a plastic enclosure, or similar reason), that you need to re-establish the connection to the GEC.
Additional question:
If your inverter has a GEC terminal inside it, that is also continuous with its metal enclosure, can this suffice? Or do you need an additional bonding bushing inside the inverter specifically because of the GEC?
The reason I ask, is that the space is limited inside a string inverter's cabinet. And it is difficult to get a bonding bushing in there, with its lug accessible. If the standard locknuts alone establish electrical continuity, and the GEC is internally bonded to the inverter enclosure, then I wouldn't see the need for the bonding bushing.
I do see the need for the bonding bushing inside the inverter, given conduit stubs in a bottomless enclosure, or given a non-metal enclosure for the inverter.