Our office is comprised of 60 cubicles with the 8-wire 4 circuit arrangement seen in many of the freestanding cubicles. I have a situation where the electrician wired these using only five (5) 20A circuit breakers. He stated that there was nothing in the code that said how many receptacles per 20A CB. I have protested this stating that this should still fall under the requirements of 605.7, 210.11(A), 220.3(B)(9). Four receptacles per cubicle are available: A,B,C,&D. The way I understand that it was wired is Circuit #1 has all 60 receptacles labeled "A", #2 has all 60 "B", #3 has all 60 "C", #4 and #5 have 30 "D" each. I have stated that he needs to have 5 circuits per each A, B, C, & D for a total of 20 circuits. 120V x 20A = 2400 2400/180VA=13.333. So 13 per each 20A. 60 recetacles /13=4.62 therefore 5 circuits. Please help me in gathering all pertinent information to disprove the electricians statements.