I'm having trouble understanding when it is required to have an OCPD on my PV output conductors. (NEC 2008 and NEC 2011)
I have two systems that were designed by someone else and i am the EC installing the PV system. They are both for residential applications at two different homes and less than 10kW. Both inverters are mounted outside next to the meter. The only conductors that will enter the house are the inverter output conductors to the back-fed breaker in the panel (Load-side connection)
The first is a transformer-less inverter and is an "Ungrounded Photovoltaic Power System". Following 690.35 am i correct that I will always have to have an OCPD in my DC positive and negative PV output conductors at DC disconnect before the inverter? Voltage is about 400VDC per string and has two PV output strings going to inverter, 8 Isc per string. Calculating with 690.8(A)1 and (B)1 with 156% x 8 = 12.48 amp conductor/OCPD.....?
The second design is exactly the same but with a "transformer" type inverter and will have the negative conductors grounded. The current design only shows the positive conductors being disconnecting in the DC disconnect and shows no OCPD anywhere in the PV DC side. I'm looking at 690.9(A) Exception, and i have no strings in parallel and no backfeeding possible. Is this compliant?
Thank you,
I have two systems that were designed by someone else and i am the EC installing the PV system. They are both for residential applications at two different homes and less than 10kW. Both inverters are mounted outside next to the meter. The only conductors that will enter the house are the inverter output conductors to the back-fed breaker in the panel (Load-side connection)
The first is a transformer-less inverter and is an "Ungrounded Photovoltaic Power System". Following 690.35 am i correct that I will always have to have an OCPD in my DC positive and negative PV output conductors at DC disconnect before the inverter? Voltage is about 400VDC per string and has two PV output strings going to inverter, 8 Isc per string. Calculating with 690.8(A)1 and (B)1 with 156% x 8 = 12.48 amp conductor/OCPD.....?
The second design is exactly the same but with a "transformer" type inverter and will have the negative conductors grounded. The current design only shows the positive conductors being disconnecting in the DC disconnect and shows no OCPD anywhere in the PV DC side. I'm looking at 690.9(A) Exception, and i have no strings in parallel and no backfeeding possible. Is this compliant?
Thank you,