Looking for some enlightenment regarding short circuit current in NYC. The installation in question is very typical; it's a ConEd Secondary Service with (6) 265/460V transformers, network protectors, and (6) 4000A Service Switchgear Lineups. There are no main devices on any of the services (also very typical for NYC).
Con Edison gives you a maximum available fault current from their network of 200K. It may actually be much lower than this but in my experience ConEd won't budge on this value. The problem is, the maximum SCCR rating of Service Switchgear is 200K, you can't get a UL listed line-up with an SCCR higher than this. Our fuses are rated for 300KAIC, but the bus bracing is only 200K. When you take into account motor contribution, your available fault current at the Service will always be more than 200K!!
Wondering if anyone knows how to get around this from a code or technical standpoint. Adding a main with a current limiting fuse is not an option. Help!
Con Edison gives you a maximum available fault current from their network of 200K. It may actually be much lower than this but in my experience ConEd won't budge on this value. The problem is, the maximum SCCR rating of Service Switchgear is 200K, you can't get a UL listed line-up with an SCCR higher than this. Our fuses are rated for 300KAIC, but the bus bracing is only 200K. When you take into account motor contribution, your available fault current at the Service will always be more than 200K!!