New house water bond

Status
Not open for further replies.

torch0395

Member
Location
New York
Occupation
Pool technician
Just bought a new house with a well water system. Can’t seem to find where/if they bonded the copper piping system in the house. So I was going to bond it using 4 guage wire to the main panel. However, the ground wire for the main panel is exposed outside and it would be easier to run it to that. Can’t I just bond the bare copper water bond wire to the bare copper ground wire?
 

tom baker

First Chief Moderator
Staff member
How have you determined that the GEC is a 4 AWG?
Here are the appropriate code sections:
250.8 bonding the two GECs
250.53 C bonding jumper
250.64 GEC installation

The water pipe bond can be a GEC or bonding conductor, depending on if its per 250.52 A 1 or 250.104.

This is pretty basic stuff....
 

torch0395

Member
Location
New York
Occupation
Pool technician
How have you determined that the GEC is a 4 AWG?
Here are the appropriate code sections:
250.8 bonding the two GECs
250.53 C bonding jumper
250.64 GEC installation

The water pipe bond can be a GEC or bonding conductor, depending on if its per 250.52 A 1 or 250.104.

This is pretty basic stuff....

im not sure that answer helps me at all
 