Neutral sizing for a UPS

Status
Not open for further replies.

JdoubleU

Senior Member
I am replacing a 3 phase 208 volt ups. The existing ups is fed with a 100 amp breaker. The new ups is fused at 63amps. My question is the conductors there now are sized #2 for the phase conductors but a #6 for the neutral. Is this ok concidering the neutral conductor has nearly no current on it?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I am replacing a 3 phase 208 volt ups. The existing ups is fed with a 100 amp breaker. The new ups is fused at 63amps. My question is the conductors there now are sized #2 for the phase conductors but a #6 for the neutral. Is this ok concidering the neutral conductor has nearly no current on it?

I think we need more info. Are you referring to the input side?
I think you may not have a neutral conductor on the input side (depending on the UPS type). This is likely an EGC.
 

ceb58

Senior Member
Location
Raeford, NC
You need to read to mfg. instructions. All of the Eaton 9170's I have installed the instructions called for one size bigger wire on the OCP that the NEC. I.e.: #2 on a 100 amp breaker with no mention of reducing the neutral size.
 
Status
Not open for further replies.