Neutral insulation for Generators at 13.2 kv

Status
Not open for further replies.

danedi

Member
Location
Puerto Rico
Good Morning to everyone.

I have this big question going around in my mind for a while. I am designing a paralleling system @13.2 KV for 3 generators 2 MW ea. The size of the phase conductors is 3#1/0 at 15 kv, but the neutral conductor we are designing as 1/0 AWG-600V, to be connected to a neutral resistor (this is a low resistance grounding scheme).
I can not find any place in the NEC that requires a 15kv insulation level for the neutral conductor to be connected from Xo at the generator to the LRG system. Any suggestions here?
Thanks
Daniel
 