Neutral bonding with two service rated ATS boxes

Status
Not open for further replies.

doug_s

New member
Location
Northwest IN
Does this look like the proper layout for the neutral bonding? Each transfer switch on left has a 200A breaker and becomes my new service disconnect. Therefore, the neutral bonds should be done there and no where else, correct?


My understanding of the NEC is that since my service disconnect location changes to the ATS boxes, the former main panels become sub panels. Therefore I then must add a 4th conductor dedicated for grounding the subpanels, and the neutral bonds must be broken in them (to avoid unbalanced neutral amperage from load sharing across the ground during normal operation).


Also, running just 3 wires to generator and having it use the primary service's grounding bond is valid for residential applications like this, right? (solid neutral ATS = no choice but linking generator neutral to utility neutral, and thus also it's ground - therefore no need for a 2nd ground rod @ generator pad?)

sEXJb.jpg



 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I am closing this thread, in accordance with the Forum rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.


If I have misjudged the situation, if for example this project is related to your work, then send me a Private Message. If you can show me that I am wrong, and that you are a licensed electrician (or at least a licensed apprentice), then I will reopen your post, and offer an apology for the delay and inconvenience.

A reminder to all members, if you see a questionable post, feel free to report it by clicking the
report-40b.png
button at the bottom left corner of the post.
 
Status
Not open for further replies.
Top