Say that is true, how do you you get around the requirement to secure the conduit within 3' of a termination (assuming you agree a conduit entering a conduit body represents a conduit termination, and the securing exception to 5' is not applicable)?

I would guess that from an NEC perspective the conduit body mentioned in the exception is not a termination otherwise what purpose what the exception serve?
 

Smart $

Esteemed Member
Location
Ohio
BTW, you are correct in that supports could be up to 5' on either side of the conduit body if the securing exception to 5' is applicable.
 