Time to review what labels are needed per NEC 2017.
1.
This one is new to me:
NEC 705.12(B)(2)(3)(c)
WARNING
THIS EQUIPMENT FED BY MULTIPLE
SOURCES.
TOTAL RATING OF ALL OVERCURRENT
DEVICES EXCLUDING MAIN SUPPLY
OVERCURRENT DEVICE SHALL NOT EXCEED
AMPACITY OF BUSBAR.
Is it needed on all PV systems, or any?
2.
This seems to be a good idea to apply to an Enphase CB, or dedicated solar AC combining panel. Is there any code reference for it?
PHOTOVOLTAIC CIRCUITS ONLY.
NO ADDITIONAL CIRCUITS ALLOWED
3.
This seems to have gone away:
NEC 690.35 (F)
WARNING
ELECTRIC SHOCK HAZARD.
THE DC CONDUCTORS OF THIS
PHOTOVOLTAIC SYSTEM ARE
UNGROUNDED AND MAY BE ENERGIZED
4.
Looks like the 4-line DC V and A label went away and is now just 2 lines (3 lines if charge controller)
What is the max current, 15A or 18.75, on an optimizer system?
and in general: Isc or Isc x 125%?
MAXIMUM VOLTAGE 480 V
MAXIMUM CIRCUIT CURRENT 18.75 A
Apply at DC Disconnects - NEC 690.53
5.
And, for the love of god, stop putting this on the AC side.
WARNING
ELECTRIC SHOCK HAZARD
TERMINALS ON THE LINE AND
LOAD SIDES MAY BE
ENERGIZED IN THE OPEN POSITION
Apply at DC Junction boxes, DC Disconnects
NEC 690.13(B)
1.
This one is new to me:
NEC 705.12(B)(2)(3)(c)
WARNING
THIS EQUIPMENT FED BY MULTIPLE
SOURCES.
TOTAL RATING OF ALL OVERCURRENT
DEVICES EXCLUDING MAIN SUPPLY
OVERCURRENT DEVICE SHALL NOT EXCEED
AMPACITY OF BUSBAR.
Is it needed on all PV systems, or any?
2.
This seems to be a good idea to apply to an Enphase CB, or dedicated solar AC combining panel. Is there any code reference for it?
PHOTOVOLTAIC CIRCUITS ONLY.
NO ADDITIONAL CIRCUITS ALLOWED
3.
This seems to have gone away:
NEC 690.35 (F)
WARNING
ELECTRIC SHOCK HAZARD.
THE DC CONDUCTORS OF THIS
PHOTOVOLTAIC SYSTEM ARE
UNGROUNDED AND MAY BE ENERGIZED
4.
Looks like the 4-line DC V and A label went away and is now just 2 lines (3 lines if charge controller)
What is the max current, 15A or 18.75, on an optimizer system?
and in general: Isc or Isc x 125%?
MAXIMUM VOLTAGE 480 V
MAXIMUM CIRCUIT CURRENT 18.75 A
Apply at DC Disconnects - NEC 690.53
5.
And, for the love of god, stop putting this on the AC side.
WARNING
ELECTRIC SHOCK HAZARD
TERMINALS ON THE LINE AND
LOAD SIDES MAY BE
ENERGIZED IN THE OPEN POSITION
Apply at DC Junction boxes, DC Disconnects
NEC 690.13(B)