motors and fluorescent lights

Status
Not open for further replies.

msteiner

Senior Member
Location
Maryland
How susceptible are fluorescent lights (120V) to voltage dip caused by motor starting (such as compressors in a 40-ton HVAC unit)? Should I avoid circuiting those two loads from the same panel at all cost? If I segregate the loads into different panels, they'll still be fed from the same distribution panel.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Fluorescents are probably less likely to show small dips in voltage than incandescents, due to the current-regulation of the ballast.

Besides, separate panels only increase isolation by the amount of wire between them, typically only a few feet of feeder.
 