...resistance to ground of 25-ohms or less...
I still have an issue with this. It seems to be a contradiction to other requirements of the code.
We all know electrical system grounding serves four primary purposes, if nothing else. Lightning, line surges, high-voltage cross-over, and voltage stabilizing. Is it safe to assume the the lightning aspect present the greatest concern and demand the most out of the grounding system?
If so, the NFPA 780 appears to contradict the grounding impedance need by the NEC. Per section B.3.5,
Now on another note. It is also well known that grounding of electrical systems presents an objectionable current path to the source. Ohm's Law shows the lower the ground resistance, the greater the current that can flow.
Doesn't this indicate that the lower the ground resistance, the greater the shock potential?
The final point. Lets assume you achieve a gorund resistance of 25 ohms as required by 250.56. A 40,000 ampere lightning strike imposed on the service equipment could create a potential of around 1 million volts. Lets now assume the lowest ground resistance that can be acheived is only 200 ohms. The same 40,000 ampere lightning strike could raise a potential of 8 million volts. In this case, it seems to indicate the lower the ground resistance, the safer the installtion. However, I again beleive this is really not true. Who cares what the potential rise over the system is during a lightning strike. If proper bonding is performed, all objects will will also be at the same potential and therefor there would be little danger for someone in contact with a properly bonded object.
So in conclusion, lightning creates the greatest energy event that can be imposed on an electrical system. Overall ground impedance is generally of little concern. Also, objectionable current shouldn't be acceptable for possible event. And finally, rise of potential and flash over are of no real concern if proper bonding is established.
Again, it appears that secondary provisions for lightning protection are more effective. Bonding, SPD's and other methods not even assoicated with grounding are the true protective devices and grounding really appears to be doing nothing.
I still have an issue with this. It seems to be a contradiction to other requirements of the code.
We all know electrical system grounding serves four primary purposes, if nothing else. Lightning, line surges, high-voltage cross-over, and voltage stabilizing. Is it safe to assume the the lightning aspect present the greatest concern and demand the most out of the grounding system?
If so, the NFPA 780 appears to contradict the grounding impedance need by the NEC. Per section B.3.5,
that pretty much says it all, but I will continue,Low resistance is desirable, but not essential...
Doesn't this basically indicate that ground impedance even as high as 200 ohms is of not much concern?...if the soil is of normal resistivity..., the resistance of a ground connection made by extending the conductor 3 m (10 ft) into the ground will be from about 15 ohms to 200 ohms, and two such ground connections on a small rectangular building have been found by experience to be sufficent.
Now on another note. It is also well known that grounding of electrical systems presents an objectionable current path to the source. Ohm's Law shows the lower the ground resistance, the greater the current that can flow.
Doesn't this indicate that the lower the ground resistance, the greater the shock potential?
The final point. Lets assume you achieve a gorund resistance of 25 ohms as required by 250.56. A 40,000 ampere lightning strike imposed on the service equipment could create a potential of around 1 million volts. Lets now assume the lowest ground resistance that can be acheived is only 200 ohms. The same 40,000 ampere lightning strike could raise a potential of 8 million volts. In this case, it seems to indicate the lower the ground resistance, the safer the installtion. However, I again beleive this is really not true. Who cares what the potential rise over the system is during a lightning strike. If proper bonding is performed, all objects will will also be at the same potential and therefor there would be little danger for someone in contact with a properly bonded object.
So in conclusion, lightning creates the greatest energy event that can be imposed on an electrical system. Overall ground impedance is generally of little concern. Also, objectionable current shouldn't be acceptable for possible event. And finally, rise of potential and flash over are of no real concern if proper bonding is established.
Again, it appears that secondary provisions for lightning protection are more effective. Bonding, SPD's and other methods not even assoicated with grounding are the true protective devices and grounding really appears to be doing nothing.