Need some help clarifying some things regarding mc cables .
1) how many mc cables can I run through a drywall penetration or concrete floor core between floors, I can’t seem to find any information.
2) how many mc cables can be supported from same ceiling wire of a suspended ceiling light.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
1) IDK but someone will
2) you need to install your own support wires that are identified, lay on floor and use spray paint.
Note the OP is using the support wire to a fixture to support his MC (not a ceiling grid wire).
We have always allowed that.... is it not permissible ?
(I am addressing a single cable, not multiple but it would seem that if the support wire has adequate strength multiple MCs could be supported along with the fixture)
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Note the OP is using the support wire to a fixture to support his MC (not a ceiling grid wire).
We have always allowed that.... is it not permissible ?
(I am addressing a single cable, not multiple but it would seem that if the support wire has adequate strength multiple MCs could be supported along with the fixture)
Agreed. You can put whatever you want on your own supports.
 