Main Disconnect switch with an electrical breaker

Status
Not open for further replies.

Cartoon1

Senior Member
Location
Florida
Occupation
Electrical Engineer
As shown in the attached figure. This is a main 400A breaker disconnect switch. Typically for something like this i typically see fused switches or a boxed circuit breaker. In this particular case, since the disconnect handle kit is on the breaker handle - if a short occurred will the handle switch on the breaker leg cause it from tripping correctly? Thank you
 

Attachments

  • 3.jpg
    3.jpg
    116.1 KB · Views: 23

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The breaker will still trip even with that handle interlock. Just to clarify that is a circuit breaker and not a molded case switch?
 