Luminaires in Hazardous Locations

Status
Not open for further replies.
In a fuel cell maintenance area (Class I, Division 2), what protection is required for fluorescent luminaires? My interpretation of the code (Article 501.130(B)(2) & (3)is that they must be protected from physical damage AND must utilize a method to contain sparks or parts of an exploding lamp. They do not have to be explosion proof fixtures.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Re: Luminaires in Hazardous Locations

As generalized statements, your interpretations are correct; however,I would caution that 501.130(B) requires that ALL subsections 501.130(B)(1) through 501.130(B)(6) be complied with. Some may not be applicable, but 501.130(B)(1) always is.

I would also direct your attention to Section 500.8; especially subsections 500.8(A)(1)and 500.8(B)(6)(a). The entire Section (500.8) should be read carefully though since there are many approval/marking/identification requirements necessary for luminaries in Classified locations - even if they are not required to be explosionproof.
 