low voltage conduit fill

Status
Not open for further replies.

novemberaudi

Member
Location
boston
I have a job where i have to pipe for various low voltage alarm cables. Just looking for a little advice do I just figure the area of the cables and use 40% conduit fill or is there a better way.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have a job where i have to pipe for various low voltage alarm cables. Just looking for a little advice do I just figure the area of the cables and use 40% conduit fill or is there a better way.

What NEC Article do your cables fall under?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In many cases, the NEC does not have rules covering conduit fill for low voltage cables. Many cable manufacturers have instructions that show wire fills of less than 40% and in one case that I know of limits the length of the pull to 100' of straight conduit, deduct 30' for each 90? bend.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
In many cases, the NEC does not have rules covering conduit fill for low voltage cables. Many cable manufacturers have instructions that show wire fills of less than 40% and in one case that I know of limits the length of the pull to 100' of straight conduit, deduct 30' for each 90? bend.
So if you design for the NEC maximum of 360 degrees, you can run -20 feet!
Sounds like their wire is pretty weak mechanically. That can happen with small conductors.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
So if you design for the NEC maximum of 360 degrees, you can run -20 feet!
Sounds like their wire is pretty weak mechanically. That can happen with small conductors.
I think it is a "CYA" thing on the part of the manufacturer. Like a lot of installers, we ignored the instructions, and made much longer pulls than specified on the supplied information sheet. We did not experience any cable damage issues.

The same time of issue exists in the BICSI standards. As I recall, their standard for the installation of "CAT" rated cable is the maximum pulling force is 25 pounds and this applies no matter how many cables are being installed.
 