Re: low voltage cable sizing
txturbo, amps are amps regardless of the voltage, you will need to run parallel conductors to get 750 amp capacity.
Something like 3 sets of 250 kcmil, or 2 sets of 500 kcmil will do it if your terminations are rated 75C and you use 75C wire.