low voltage cable sizing

Status
Not open for further replies.

txturbo

Member
Re: low voltage cable sizing

No.....its for the output of a electroplating rectifier.I need to connect the output buss bars to the buss bars at my plating bench.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: low voltage cable sizing

txturbo, amps are amps regardless of the voltage, you will need to run parallel conductors to get 750 amp capacity.

Something like 3 sets of 250 kcmil, or 2 sets of 500 kcmil will do it if your terminations are rated 75C and you use 75C wire.
 

bennie

Esteemed Member
Re: low voltage cable sizing

Four feet can be a mile to 12 volts. Be sure you use the figures Bob has given, plus a little more.

You will notice when maximum current is flowing in your plating tanks, the voltage will read zero on convential volt meters. Resistance is the principal concern. The lower the resistance the more available current. Heating effects are negligible due to low (eye two are).
 