Re: Lamp life too short!
Have a few thoughts in regards to this thread.
1: The 15 Watt Incandescent Lamps in recessed fixtures:
* Maybe getting too hot?
Excessive heat contributing to premature Lamp failure.
* Maybe the Lamps have only like 600 Hours Lamp Life @ 120VAC?
Run for 5 Hours each day over 120 Days (4 Months) = 600 Hours of operation.
* 15 Watt Lamp filaments may be very sensitive to inrush/start surges?
The cold Resistance of the filament will be lower than the operating (hot) Resistance.
* Possible to have >120 VAC at Lamp Starting or during operation?
May be a Transient case of higher than 120 VAC, or maybe the Switch controlling these Lamps is bouncing too much.
I like the CFL option (Compact Fluorescent Lamps). 15 Watt CFL will be as bright as a 60 Watt A17 Incandescent Lamp, designed for and running at 120VAC. The CFLs will last longer than conventional Incandescent Lamps.
Drawbacks are the unit type Ballast (longer overall length... only a visual drawback!), and the Color temperatures available are at most only around 2700K (maybe 3000K). If "Warm White" is OK to you, then the Color Temperature is no issue.
AFAIK, the "Old Lamp Life Extender Device" mentioned earlier was a Full Wave Bridge Rectifier, incorporated within a medium base screwshell type adapter.
If not a Full Wave Bridge, then maybe a single Diode Half Wave Rectifier - possibly with a ballasting Resistor.
Per the Common Conductor of a 4 wire 3? Wye Transformer setup;
Have a few thoughts towards these setups, as follows:
* Per use of a 4 Wire Multiwire circuit with all Lines having pure Resistance loads of equal value:
The Common Grounded Conductor will carry nearly zero Current.
* Per use of a 4 Wire Multiwire circuit with all Lines having pure Resistance loads of different values:
The Common Grounded Conductor will carry the "Vector Sum" of the Line(s) Current. More than zero, but less than the highest Line's Current.
* Per use of a 4 Wire Multiwire circuit with all Lines having NON pure Resistance loads of any value (AKA "Non-Linear Loads):
The Common Grounded Conductor will carry nearly the same level of Current which is found on the Line with the highest level of Current.
Just my 2?
Scott35
p.s. this common conductor loading stuff is covered a little more in detail, within my reply to the
Number Of Current Carrying Conductors Thread.