Is this required

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since the largest GEC ever required is #3/0 the answer is no. The conductor sizes of that ground detail are not required.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Leaving aside the GEC size, and only speaking of code ..

It's required in part, and in part it depends.

The neutral to ground bond (Main Bonding Jumper) is required in all situations.

If the existing GEC installation lands the GEC(s) in the other service disconnect(s), then you must also bring a GEC tap to the new disconnect, as shown or similar to the drawing. The manner shown could be fine if the main building ground bus meets requirements. It is not the only place you could terminate the new GEC (or GEC tap) on the ground end.

If the existing GEC is connected further towards the utility, for example in the 'existing service end box', then the disconnect doesn't need its own GEC or GEC tap.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMHO... It might be required by job spec by the customer, or by AHJ, but not required by code.
I think that was the OP's question, is it required by the NEC. Note 1 has many things that are not required, same with Note 4. Since conduit protection is not required add Note 3 to the list too.
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
If it's shown in the Contract Documents, then it is required for this project as long as it isn't a code violation. The NEC is not a design guide.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I see a number of issues with drawing the OP posted. For starters, there should not be a EGC on the supply side. Maybe a SSBJ depending on how this done but not a #1 EGC.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Two 350 cu seems kind of excessive too.

I think this drawing was done by someone who does not know what they are doing and just made everything overkill to cover that lack of knowledge.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Two 350 cu seems kind of excessive too.

I think this drawing was done by someone who does not know what they are doing and just made everything overkill to cover that lack of knowledge.
Maybe, but there is no indication on line drawing as to the length of the run that might need to increase size for voltage drop. Depending on the min size that might be installed then the EGC would be increased proportionally to the increase in the current carrying conductors, so the #1 EGC might be undersized.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Maybe, but there is no indication on line drawing as to the length of the run that might need to increase size for voltage drop. Depending on the min size that might be installed then the EGC would be increased proportionally to the increase in the current carrying conductors, so the #1 EGC might be undersized.
Since there is a 400 amp OCPD and over 600 amps worth of conductors I would say that the ungrounded conductors have been increased in size therefore the #1 may be too small. Given the other errors with this drawing I'm not surprised the designer got that wrong too.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Yeah. #1 is 60% larger than #3. 700mcm is only 40% larger than 500mcm.
Thanks for doing the math. Just eyeball like @infinity said. Was throwing out the possibility of oversize for voltage drop and then need to follow up with the EGC increase proportionally. Something most miss.

Something I see often is someone using 250kcmil for whatever reason when 4/0 would suffice but never increase the EGC proportionally from the #4.

Question would be if the math made for conductor proportion that is slightly larger than the 2 sizes up do you increase to 3 sizes or just use the 2 size increase, or use the over .5 rounding rule?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Just eyeball like @infinity said.
For my original eyeball I thought that since this installation uses parallel conductors if you used the minimum required size of parallel #3/0's (400 amps) the #1 is too small when applying 250.122(B). The minimum size would be #4/0. I'm rusty at these calculations so check my math.

#3/0=167800 cm
3/0*2=335600 cm
350,000*2=700000 cm

700 kcmil/335.6 kcmil = 2.09 ratio of size increase
#3=52620 cm
52620*2.09= 109.7 kcmil
#1/0= 105.6 kcmil too small
#2/0= 133.1 kcmil correct size.

Edit: I corrected the error, thanks Tulsa!
 
Last edited:

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
For my original eyeball I thought that since this installation uses parallel conductors if you used the minimum required size of parallel #3/0's (400 amps) the #1 is too small when applying 250.122(B). The minimum size would be #4/0. I'm rusty at these calculations so check my math.

#3/0=167800 cm
3/0*2=335600 cm
350,000*2=700000 cm

700 kcmil/335.6 kcmil = 2.09 ratio of size increase
#1=83690 cm
83690*2.09= 175 kcmil
#3/0= 167.8 kcmil too small
#4/0= 174912 correct size.
You based it off of the #1 cu.
Wouldn't you base it off the minimum EGC required for the 400 amp. Which would be #3 cu @ 2.08581 ?
52620* 2.08581= 109,755.3222
2/0@ 133,100 CM
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You based it off of the #1 cu.
Wouldn't you base it off the minimum EGC required for the 400 amp. Which would be #3 cu @ 2.08581 ?
52620* 2.08581= 109,755.3222
2/0@ 133,100 CM
Yes you would. As I said a little rusty but my initial guess that the #1 could be too small was accurate. I made the correction to my last post.
 
Last edited: