I'm buying a house. It has an outdoor AC compressor on a #10 wire with a 50amp breaker.
My inspector says it should be a 30amp breaker.
The electrician who installed it says its within the NEC code based on these facts:
1) 310.16 says up to 40amp is ok on a #10 wire.
2) 440.22 says the breaker can be 175%, up to 225%, of the rated load current of the compressor.
3) At 175%, a 30amp wire can support a 50amp breaker ( 30 * 1.75 = 52.5 ).
It sounds like he is mistakenly using the rated WIRE current instead of the rated LOAD current.
And so a 50amp breaker would only be allowed on a device with 28.5 RLC (or 22.5 RLC at 225%).
If the RLC of the AC compressor really was a full 28.5amp, would anyone use a #10 wire, even though 'technically' it appears to be legal?
Or do most AC installations require the 225% rule? And if so, would you still put a 22.5+ RLC on a #10? When do you cut over to a #8?
I wish I had the running current but I don't close until Wednesday and can then get the spec's on the compressor.This is a home AC compressor cooling 2800 sq feet.
My main concern - does this sound safe?
Thanks for your help!
Todd
Todd