Inverters at rack or house?

Status
Not open for further replies.

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Hi,

I was wondering if I could get some opinions. Is it better to place the inverters at the rack of a ground mount and have the ac run back to the house? Or is it better to have the dc run from the rack to the house, and place the inverters at the house?
 

SolarPro

Senior Member
Location
Austin, TX
All else being equal, it is best to run the dc back to the house. Typically the array operating voltage is higher than the ac grid voltage, so you have less voltage drop. Also, excessive voltage drop in an inverter ac output circuit, can result in inverter nuisance tripping. Connecting to the grounding electrode system at the house is easier if the inverter is near the main service. Etc.
 
Status
Not open for further replies.
Top