Intrinsicaly safe Wiring

Status
Not open for further replies.

ed_man

Member
I need to run intrinsicaly safe control wiring (Start/Stop + Speed Potentiometer) from an unclassified location to the operator station in a Class 1, Div 1, industrial location with a dropped ceiling. I was thinking of running multiconductor PLTC above the ceiling. Would this be appropriate? I referenced 504.20, 336.10(7) and 504.30. I'm not sure if this would pass 504.30 if the rest is ok. I know a seal is needed.

Application
I am replacing a mixer that has an across-the-line starter with a new unit that has a VFD to run the motor. So, the power wiring is existing.

Any suggestions or guidance would be appreciated.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Art 336 does not apply to Type PLTC; it is an Article 725 construction and must be installed consistent with that Article as well as 504.30. Do you have the manufacturer's control drawing? Is the dropped ceiling a plenum area?

The odds are fairly high that what you want to do is acceptable but you need to review Art 725.
 