Lets suppose I have a new home being built and the specifications call for a pool. Due to utility location, the service will be on the opposite side of the house as the lighting and appliance panelboard.
I will be placing a pool equipment panelboard at the equipment location served by a feeder from the house lighting and appliance panelboard.
Per 680.25, it appears that I am required to have an insulated grounding conductor and that my wiring method must be a raceway. Also, the main feeder from the outside service disconnect to the lighting and appliance would also have to comply.
I have seen many installations that use SER cable from the service disconnect to the lighting and appliance panelboard, form that point I have also seen NM to the pool equipment. Is this a violation?