how do I ground a 25V circuit?

Status
Not open for further replies.

unsaint34

Member
I have 277/480 Y at work and I need to hook up an exit sign that uses 25V. So, I am planning to use a transformer, I assume 277/25V transformer.
I looked up the code book which said, I need to ground a system if it is less than 50V, and if it is fed by a supply system of more than 150V.
But, how do I system ground the secondary side, which is the exit sign? Run a grounding wire to concrete? Even if I did that, what do I connect it to? All the electrodes, the building metal structure, and water pipes are being used as electrodes for the building.

Am I wrong about the code?

Jon


What is the "objectionable current" at the code
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: how do I ground a 25V circuit?

I can't believe that a new 120v or 277v exit sign would cost more than a transformer and the work necessary to install it and make the 24v sign work.

-Hal
 

peter d

Senior Member
Location
New England
Re: how do I ground a 25V circuit?

Perhaps there is some special circumstance why this 25 volt sign is necessary.

What say you, Jon?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: how do I ground a 25V circuit?

Jim,
The 277 to 25 volt transformer is an SDS and requires a grounding electrode and grounding electrode conductor. This is required by 250.20(A)(1).
Don
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: how do I ground a 25V circuit?

Jon,
Even if I did that, what do I connect it to? All the electrodes, the building metal structure, and water pipes are being used as electrodes for the building.
You run the GEC from the transformer to the nearest available grounding electrode. It doesn't matter if that grounding electrode is already in use for another system. You many not need a GEC if you can use the exception to 250.30(A)(2), but you will need a bonding jumper. This jumper would connect to EGC for the 277 volt circuit.
Don

[ March 09, 2005, 10:39 PM: Message edited by: don_resqcapt19 ]
 