horn/strobes mounting height

Status
Not open for further replies.

mzeleny

Member
Code require to install horn/strobe at 6'-8" AFF.
If ceiling height in the basement of apartment building is lower than 6'-8", can these devices be installed lower?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: horn/strobes mounting height

Yes, they can be lower. As far as I know the 6'8" (or 7' to the top) is an ADA driven requirement.

Roger
 

inspector 102

Senior Member
Location
Northern Indiana
Re: horn/strobes mounting height

NFPA 72, Section 6-4.4 also states that wall mounted apliances shall have their bottoms at heights above the finished floor of not less than 80 inches and no greatyer than 96 inches. Ceiling mounted appliances are covered by a table describing room size and candela output.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: horn/strobes mounting height

Mzeleny, there you have it, you can't have a "horn strobe" in this basement or any crawl space, so if it is required, all that can be done is to condemn the building. :( :D :D

Roger
 

bwyllie

Senior Member
Location
MA
Re: horn/strobes mounting height

I typically specify these devices to be mounted 80"AFF or 6" below ceiling height, which ever is less.
 
Status
Not open for further replies.
Top