OK, I'm specifying a 12KV feeder for a 2500KVA transformer. I was wondering if this sounds like the right way to go:
2500KVA/12KV/sqrt(3) *1.25 = 150 amps primary OCP. So I would use #2 copper XLP based on table 310.77. (I never know if this table applies to 3 conductors in a single burried conduit).
From the notes on table 310.64, I would assume it would be safe to use 133% although I'm not sure if the loop I am taking power from is grounded or not.
From Southwire, I got a cut sheet on their XLP cable:
http://appprod.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet105
It looks like #2 has about a 1" diameter. Thats 0.79 square inches. If I put 3 of these into a single conduit, I need 2.4% of conduit area at 40% fill. So it looks like a 3" conduit will work (see edit below).
Or would it be better to install one cable in each of 3 conduits? Can I do that with metal conduit, or would that have to be PVC?
A couple of more questions: Whats the difference between XLP and EPR? Would one be better for this than the other? How about the difference between "Tape" and "Wire" sheilds?
Steve
Edit:
I already see that jambing might be a problem, so it looks like it is 4" conduit.
2500KVA/12KV/sqrt(3) *1.25 = 150 amps primary OCP. So I would use #2 copper XLP based on table 310.77. (I never know if this table applies to 3 conductors in a single burried conduit).
From the notes on table 310.64, I would assume it would be safe to use 133% although I'm not sure if the loop I am taking power from is grounded or not.
From Southwire, I got a cut sheet on their XLP cable:
http://appprod.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet105
It looks like #2 has about a 1" diameter. Thats 0.79 square inches. If I put 3 of these into a single conduit, I need 2.4% of conduit area at 40% fill. So it looks like a 3" conduit will work (see edit below).
Or would it be better to install one cable in each of 3 conduits? Can I do that with metal conduit, or would that have to be PVC?
A couple of more questions: Whats the difference between XLP and EPR? Would one be better for this than the other? How about the difference between "Tape" and "Wire" sheilds?
Steve
Edit:
I already see that jambing might be a problem, so it looks like it is 4" conduit.
Last edited: