All the way to the transformer? Or just to the service? I thought you said above the service was #6?
It was thought that it was #6, but in fact #8 from the street to the service panel.... ~ 15' length. From the transformer to the street hookup, I believe is #0 just based on the size.... as there are no outer markings.
So...
#0 Transformer to Street hookup ~100'
#8 Street hook up to Service Panel (with 2 - 40amp breakers!) ~ 15'
#8 Service Panel to Breaker Panel ~50'
#8 Breaker Panel to Inverter ~50'
I calculate that your voltage drop along the inverter output will be a volt or two higher with #8 than with, say, #4. If this were the US and it was a 100A service with a #2 feeder to the sub then you'd probably have a couple extra volts of cushion. Still, it doesn't change the nature of the problem. It's about 1% Vdrop. I'm sure I've ever seen an nominal 240V supply read higher than about 255V in my work. (Which has been all in fairly urban areas in the states, to be sure.)
Will look into pulling #4 from street hookup to breaker to inverter with the hopes of at least getting in down a few volts as this might be enough to stop the inverter from tripping.
Still working on getting electric company to agree a problem exists.
Thanks for all the input!