A 2.5mm square twin copper cable 20m long supplies a heating appliance having three elements each of resistance 57.6 ohms. If the elements are arranged such that two are in series and the third is in parallel with these two, calculate: (a) the resistance of the cable; and (b) the total resistance of the whole circuit. (p for copper is 17 x 10to the power of 6 ohms)?
I know the answers are (a) 0.272 ohms and (b) 38.672 ohms, I am just not sure how to get there, would be grateful for any insight?
thanks
mpross
midwest
Equation
Equation
mimi,
For the resistance R of the cable:
R = p*L / A
= ((17*10^-6)*40) / .0025 = .272 Ohms
For the resistance of the whole circuit:
The two resistors in series just add>> 57.6*2 = 115.2
...now for the parallel resistor: use the "product over sum" rule:
(115.2*57.6)/(115.2+57.6) = 38.4 Ohms
...38.4 + .272 = 38.672 Ohms
Hope this helps
-mpross
mpross
midwest
Resistance of wire
Resistance of wire
georgestolz,
I found the conductivity of Cu to be .596 x 10^6 / (cm Ohms). Conductivity is the inverse of resistivity. For a better explanation than what I could give in this forum, check out this site. It has a ton of good info!
http://230nsc1.phy-astr.gsu.edu/hbase/hframe.html
hyperphysics > Electricity and Magnetism > Resistor
Have fun with the site!
mpross