Help with 277 V lights on 3 ph system

Status
Not open for further replies.
Trying to run 2 277 Volt 1000 Watt HID Floods on one leg of a 3 ph 480 Volt 100 Amp fused disconnect which is running 2 30 Amp 3 ph AC units. When I tap into one leg of the power it zero's out my voltage on the leg im trying to use and raises the voltage on the other 2 legs. Wondering if it is just throwing it out of balance? What to do? Should I try and run the 2 fixtures from 2 different legs to help balance the load?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Would this be an ungrounded delta? Where are you picking up the neutral for the 277? And why did you pick this source for your supply?
 
Not sure if it is delta? The meter is located next to the disconnect it is an older system. There is a solid copper ground which I have hooked the neutral to coming off of the meter.
 

stevebea

Senior Member
Location
Southeastern PA
Trying to run 2 277 Volt 1000 Watt HID Floods on one leg of a 3 ph 480 Volt 100 Amp fused disconnect which is running 2 30 Amp 3 ph AC units. When I tap into one leg of the power it zero's out my voltage on the leg im trying to use and raises the voltage on the other 2 legs. Wondering if it is just throwing it out of balance? What to do? Should I try and run the 2 fixtures from 2 different legs to help balance the load?

No..... if this is a disconnect for AC units its very doubtful you have a neutral. A 100A disconnect is not the place to look for a feed for 277V lighting.
 

Jnas480

Member
Location
Eastern CT
It does sound like you have open delta One of phase is grounded.

You are better off using a ballast kit for 480 volts. and this will solve your problem.

Good Luck
 

LEO2854

Esteemed Member
Location
Ma
Trying to run 2 277 Volt 1000 Watt HID Floods on one leg of a 3 ph 480 Volt 100 Amp fused disconnect which is running 2 30 Amp 3 ph AC units. When I tap into one leg of the power it zero's out my voltage on the leg im trying to use and raises the voltage on the other 2 legs. Wondering if it is just throwing it out of balance? What to do? Should I try and run the 2 fixtures from 2 different legs to help balance the load?

Welcome to the forum:)
Should I try and run the 2 fixtures from 2 different legs to help balance the load?[/
Yes if you have two 1000 watt 277 volt HID Floods why not try to balance out the load.
 
Last edited:

LEO2854

Esteemed Member
Location
Ma
Trying to run 2 277 Volt 1000 Watt HID Floods on one leg of a 3 ph 480 Volt 100 Amp fused disconnect which is running 2 30 Amp 3 ph AC units. When I tap into one leg of the power it zero's out my voltage on the leg im trying to use and raises the voltage on the other 2 legs. Wondering if it is just throwing it out of balance? What to do? Should I try and run the 2 fixtures from 2 different legs to help balance the load?

Welcome to the forum:)
Should I try and run the 2 fixtures from 2 different legs to help balance the load?[/
Yes if you have two 1000 watt 277 volt HID Floods why not try to balance out the load.Should I try and run the 2 fixtures from 2 different legs to help balance the load?[/

sorry for the double post my computer is having trouble
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Welcome to the forum:)
Should I try and run the 2 fixtures from 2 different legs to help balance the load?[/
Yes if you have two 1000 watt 277 volt HID Floods why not try to balance out the load.
If this is an ungrounded delta system, as it appears to be, you can't run 277 volt loads from it.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If it's 480v Delta, you can't suppy 277v loads from it anyway. You'd need to derive a neutral or use a transformer.
 